    This is a real puzzler...

    ...yesterday we lost a "circuit" in the house. I say "circuit" since the affected items are all over the place:

    2nd floor - hall lights
    1st floor - front hall lights, living room outlets, outside lights
    basement - some overhead lights

    ...all no longer worky.

    I checked the main panel, all breakers OK. To be sure I reset each breaker (off then on) several times, no help.

    Next I checked each breaker to see exactly what was connected to it (since the legend printed on the panel was a little cryptic), in an attempt to determine which breaker is controlling the affected circuit. Each breaker was verified working properly (stuff went out and came back on as each breaker was toggled). After completing this exercise I still have no clue to which breaker(s) the affected circuit is linked to. FYI - My panel has no GFI breakers installed.

    All house appliances are working normally...no dimmed lights or other weirdness. The house was built in 1973, has modern wiring and one panel box. In my past experience electrical issues were always pretty simple to solve, this one has me stumped.

    What am I missing?
    #1
  2. Al Tuna

    Al Tuna Off The Hook

    Joined:
    Nov 24, 2006
    Oddometer:
    26,217
    Location:
    VOTB
    Call the power co, tell them you you may have lost a phase. Will the oven elements heat up?
    #2
  3. rapidoxidationman

    rapidoxidationman Easily trainable

    Joined:
    Apr 18, 2006
    Oddometer:
    13,601
    Location:
    The Teton Rockies
    Sounds like you lost one leg of your 220V in.

    If you have a voltmeter and the knowledge to use it without getting thrown across the room, check for 220V at either a 220V outlet or inside the circuit breaker box.
    #3
  4. Jayrod1318

    Jayrod1318 Poster

    Joined:
    Jun 14, 2011
    Oddometer:
    1,755
    Location:
    Here and there and stuff.
    If you did lose a leg, if you have any appliances like a electric hot water heater you will see some voltage on the dead leg causing untold head scratching and cursing. Damhik

    And in the mean time unplug everything! This can damage electronics.
    #4
  5. Al Tuna

    Al Tuna Off The Hook

    Joined:
    Nov 24, 2006
    Oddometer:
    26,217
    Location:
    VOTB
    And cause a fire.
    #5
  6. Garbln

    Garbln Been here awhile

    Joined:
    Sep 28, 2007
    Oddometer:
    544
    Location:
    Mpls, MN
    Try resetting the main breaker on your breaker box, one phase may have popped. Sometimes shutting them completely off than on again will do the trick. If that doesn't do it call the power Co NOW! Don't ask me how I know how much damage a gopher can cause when you have underground service!
    #6
  7. dtysdalx2

    dtysdalx2 The only easy day was yesterday...

    Joined:
    Aug 1, 2004
    Oddometer:
    36,755
    Location:
    Moneyapolis, MN
    Burned wire or bad connection to outlets?
    #7
  8. Twilight Error

    Twilight Error Going nowhere slowly

    Joined:
    May 18, 2002
    Oddometer:
    22,878
    Location:
    The Submarine Mines
    You may be able to determine a dropped phase by looking at the circuits that don't work. A panel is set up so the phases alternate A/B/A/B/A... down each side. If every other circuit works, you do indeed have a dropped phase and it needs to get sorted ASAP.
    #8
  9. River

    River Gee

    Joined:
    Feb 7, 2007
    Oddometer:
    352
    Location:
    Red Deer, AB
    It's not because I'm an electrician, but call an electrician:wink:
    #9
  10. River

    River Gee

    Joined:
    Feb 7, 2007
    Oddometer:
    352
    Location:
    Red Deer, AB
    There is a possibility that there is a GFI receptacle in the circuit. They can be configured in such a way that everything downstream of the receptacle is protected by the GFI. This would not normally be done with the interior and exterior devices, but I have seen some goofy configurations in the past. You would simply have to reset the recptacle. Other than any obvious conditions, there could be loose connections(common with older aluminum wiring) that have burnt off in a junction box somewhere. These loose connections are the common cause of electrical fires.
    Whatever you do, respect the voltage:D
    #10
  11. Dr. John

    Dr. John Been here awhile Supporter

    Joined:
    Apr 21, 2007
    Oddometer:
    307
    Location:
    Central CT
    First buy,or borrow a cheap voltage tester and check the outgoing side of each breaker. If you have 110 at all your single breakers, then test your double pole breakers for 220. A lot of people (electricians included) will use the quick wire plug in feature on outlets and switches ,that when overheated multiple times will allow the pushed in wire to either back out slightly ,or cause the spring brass that held tension on the conductor to lose it's grip. So it's possibly a circuit that starts out fine and goes to hell in a downstream plug or switch. Now the fun begins. Start at the first light or outlet not working,and closest proximity to your panel take it out of the wall and use your tester to check for voltage on both sides. It's a pain in the ass search for things like this,but if it's not a breaker,or a lost leg coming in (doubtful too many things working in the house) it's a good way to learn your house,and cheaper than hiring someone who will do the same.By the way,if you can find a non digital tester for this job you'll be happier with the results as digitals can give phantom voltage readings that will drive you nuts. Be careful,proceed slowly,and good luck.
    #11
  12. rgoers

    rgoers Been here awhile

    Joined:
    Apr 27, 2011
    Oddometer:
    372
    Location:
    Northern Utah
    My thoughts exactly! The Bozo that wired my house put the outside outlets, the garage, and the outlet over my water heater in my utility room all on the same GFI. It justs happens that my internet feed is in the utility room too, so when something pops the garage GFI, my internet goes out. He also wired all the bathrooms on one GFI, so when the powder room pops, I have to reset it on the opposite end of the house, in the master bathroom. Idiot...
    #12
  13. Jayrod1318

    Jayrod1318 Poster

    Joined:
    Jun 14, 2011
    Oddometer:
    1,755
    Location:
    Here and there and stuff.
    The house must have burnt to the ground. No response from the OP.:eek1
    #13
  14. Heloflights

    Heloflights Been here awhile

    Joined:
    Apr 6, 2008
    Oddometer:
    319
    Location:
    Marion, VA
    Power Co was just here, both 120V phases and neutral checked out fine.

    Turns out several of the affected circuits appear to be suffering from low voltage (~80-100) which explains why bulbs are not lighting up. Power co tech was of the opinion that perhaps the main panel breaker may be crapping out/acting flaky, electrician on call for tomorrow....

    ...never a dull minute....
    #14
  15. River

    River Gee

    Joined:
    Feb 7, 2007
    Oddometer:
    352
    Location:
    Red Deer, AB
    :thumb
    #15
  16. burnham

    burnham Adventurer

    Joined:
    Dec 26, 2011
    Oddometer:
    93
    Location:
    vacation
    Snap the main breaker on and then off a few times. Do it with a little vigor. Sometimes that will correct the problem for a short time, and let you know what the problem is. Sometimes the breaker won't stay on after, so be warned. Is it a Federal Pacific brand panel?

    If you have the original 1973 electric service it's probably due to be replaced anyway.
    #16
  17. beac83

    beac83 Adventurer

    Joined:
    Feb 24, 2012
    Oddometer:
    23
    Location:
    Peekskill, NY
    Did anyone do any work on the system recently?

    Replace a switch, light, outlet? If so, possibly a loose connection/broken wire.

    The house was built in 1973. Hopefully it doesn't have aluminum wire in the walls. (some jurisdictions still allowed Aluminum wiring back then)
    #17
  18. Heloflights

    Heloflights Been here awhile

    Joined:
    Apr 6, 2008
    Oddometer:
    319
    Location:
    Marion, VA
    Tried resetting the main panel breaker several times before the power co arrived (some folks mentioned this technique can help restore a dropped phase) and behold the circuit did pop back to life for a few minutes....then keeled over.

    No alum wire in the house, nor any recent electrical work performed.

    I have a Cutler Hammer main panel, the main breaker is a C-H # CC2150 150A 2 pole 240VAC, looks like it has been there since Jesus was a baby. I am trying to imagine how a breaker would fail in this manner, I figured it would just die, not create weirdness like I am seeing...
    #18
  19. Twilight Error

    Twilight Error Going nowhere slowly

    Joined:
    May 18, 2002
    Oddometer:
    22,878
    Location:
    The Submarine Mines
    A high resistance connection in the breaker would cause a voltage drop like that. The big danger is resistance = heat, enough heat can overcome the insulation and start an electrical fire in the panel.
    #19
  20. Heloflights

    Heloflights Been here awhile

    Joined:
    Apr 6, 2008
    Oddometer:
    319
    Location:
    Marion, VA
    ...wouldn't the voltage drop due to high resistance be uniform throughout all circuits in the house?