Bluhduh Any electricians in the house?

This is a real puzzler...

...yesterday we lost a "circuit" in the house. I say "circuit" since the affected items are all over the place:

2nd floor - hall lights
1st floor - front hall lights, living room outlets, outside lights
basement - some overhead lights

...all no longer worky.

I checked the main panel, all breakers OK. To be sure I reset each breaker (off then on) several times, no help.

Next I checked each breaker to see exactly what was connected to it (since the legend printed on the panel was a little cryptic), in an attempt to determine which breaker is controlling the affected circuit. Each breaker was verified working properly (stuff went out and came back on as each breaker was toggled). After completing this exercise I still have no clue to which breaker(s) the affected circuit is linked to. FYI - My panel has no GFI breakers installed.

All house appliances are working normally...no dimmed lights or other weirdness. The house was built in 1973, has modern wiring and one panel box. In my past experience electrical issues were always pretty simple to solve, this one has me stumped.

What am I missing?
__________________
Cheers,


Heloflights

2008 R1200GSA
Heloflights is offline   Reply With Quote
Old 05-07-2013, 03:23 PM   #2
Al Tuna
PUI... Deal with it
 
Al Tuna's Avatar
 
Joined: Nov 2006
Location: Moran Nation
Oddometer: 11,700
Quote:
Originally Posted by Heloflights View Post
This is a real puzzler...

...yesterday we lost a "circuit" in the house. I say "circuit" since the affected items are all over the place:

2nd floor - hall lights
1st floor - front hall lights, living room outlets, outside lights
basement - some overhead lights

...all no longer worky.

I checked the main panel, all breakers OK. To be sure I reset each breaker (off then on) several times, no help.

Next I checked each breaker to see exactly what was connected to it (since the legend printed on the panel was a little cryptic), in an attempt to determine which breaker is controlling the affected circuit. Each breaker was verified working properly (stuff went out and came back on as each breaker was toggled). After completing this exercise I still have no clue to which breaker(s) the affected circuit is linked to. FYI - My panel has no GFI breakers installed.

All house appliances are working normally...no dimmed lights or other weirdness. The house was built in 1973, has modern wiring and one panel box. In my past experience electrical issues were always pretty simple to solve, this one has me stumped.

What am I missing?
Call the power co, tell them you you may have lost a phase. Will the oven elements heat up?
__________________
Southeast Weather Map

Under construction
Al Tuna is offline   Reply With Quote
Old 05-07-2013, 03:25 PM   #3
rapidoxidationman
Easily trainable
 
rapidoxidationman's Avatar
 
Joined: Apr 2006
Location: The Teton Rockies
Oddometer: 8,078
Sounds like you lost one leg of your 220V in.

If you have a voltmeter and the knowledge to use it without getting thrown across the room, check for 220V at either a 220V outlet or inside the circuit breaker box.
__________________
Quote:
I know I'm feeling badly when I have no interest in speeding
Patrick
rapidoxidationman is offline   Reply With Quote
Old 05-07-2013, 05:04 PM   #4
Jayrod1318
Poster
 
Jayrod1318's Avatar
 
Joined: Jun 2011
Location: Here and there and stuff.
Oddometer: 1,522
If you did lose a leg, if you have any appliances like a electric hot water heater you will see some voltage on the dead leg causing untold head scratching and cursing. Damhik

And in the mean time unplug everything! This can damage electronics.
__________________
Jayrod1318 is offline   Reply With Quote
Old 05-07-2013, 05:06 PM   #5
Al Tuna
PUI... Deal with it
 
Al Tuna's Avatar
 
Joined: Nov 2006
Location: Moran Nation
Oddometer: 11,700
Quote:
Originally Posted by Jayrod1318 View Post
If you did lose a leg, if you have any appliances like a electric hot water heater you will see some voltage on the dead leg causing untold head scratching and cursing. Damhik

And in the mean time unplug everything! This can damage electronics.
And cause a fire.
__________________
Southeast Weather Map

Under construction
Al Tuna is offline   Reply With Quote
Old 05-07-2013, 05:19 PM   #6
Garbln
Gnarly Adventurer
 
Joined: Sep 2007
Location: Mpls, MN
Oddometer: 438
Try resetting the main breaker on your breaker box, one phase may have popped. Sometimes shutting them completely off than on again will do the trick. If that doesn't do it call the power Co NOW! Don't ask me how I know how much damage a gopher can cause when you have underground service!
Garbln is offline   Reply With Quote
Old 05-07-2013, 07:03 PM   #7
D.T.
One wheel wonder...
 
D.T.'s Avatar
 
Joined: Aug 2004
Location: Moneyapolis, MN
Oddometer: 9,428
Burned wire or bad connection to outlets?
__________________
Quote:
Originally posted by burgerking So?
Holland is about the most expensive country in Europe when it comes to bikes and fuel..Stop whining and go riding It's just money and you only live once...
D.T. is online now   Reply With Quote
Old 05-07-2013, 08:57 PM   #8
Twilight Error
Going nowhere slowly
 
Twilight Error's Avatar
 
Joined: May 2002
Location: The Submarine Mines
Oddometer: 22,444
You may be able to determine a dropped phase by looking at the circuits that don't work. A panel is set up so the phases alternate A/B/A/B/A... down each side. If every other circuit works, you do indeed have a dropped phase and it needs to get sorted ASAP.
Twilight Error is offline   Reply With Quote
Old 05-08-2013, 07:20 AM   #9
River
Gee
 
Joined: Feb 2007
Oddometer: 156
It's not because I'm an electrician, but call an electrician
__________________
Everyone has their own rhythm....so find it and lets jam
River is offline   Reply With Quote
Old 05-08-2013, 07:28 AM   #10
River
Gee
 
Joined: Feb 2007
Oddometer: 156
There is a possibility that there is a GFI receptacle in the circuit. They can be configured in such a way that everything downstream of the receptacle is protected by the GFI. This would not normally be done with the interior and exterior devices, but I have seen some goofy configurations in the past. You would simply have to reset the recptacle. Other than any obvious conditions, there could be loose connections(common with older aluminum wiring) that have burnt off in a junction box somewhere. These loose connections are the common cause of electrical fires.
Whatever you do, respect the voltage
__________________
Everyone has their own rhythm....so find it and lets jam
River is offline   Reply With Quote
Old 05-08-2013, 07:33 AM   #11
Dr. John
Adventurer
 
Joined: Apr 2007
Location: Central CT
Oddometer: 71
First buy,or borrow a cheap voltage tester and check the outgoing side of each breaker. If you have 110 at all your single breakers, then test your double pole breakers for 220. A lot of people (electricians included) will use the quick wire plug in feature on outlets and switches ,that when overheated multiple times will allow the pushed in wire to either back out slightly ,or cause the spring brass that held tension on the conductor to lose it's grip. So it's possibly a circuit that starts out fine and goes to hell in a downstream plug or switch. Now the fun begins. Start at the first light or outlet not working,and closest proximity to your panel take it out of the wall and use your tester to check for voltage on both sides. It's a pain in the ass search for things like this,but if it's not a breaker,or a lost leg coming in (doubtful too many things working in the house) it's a good way to learn your house,and cheaper than hiring someone who will do the same.By the way,if you can find a non digital tester for this job you'll be happier with the results as digitals can give phantom voltage readings that will drive you nuts. Be careful,proceed slowly,and good luck.
Dr. John is offline   Reply With Quote
Old 05-08-2013, 01:30 PM   #12
rgoers
Gnarly Adventurer
 
Joined: Apr 2011
Location: Northern Utah
Oddometer: 372
Quote:
Originally Posted by River View Post
There is a possibility that there is a GFI receptacle in the circuit. They can be configured in such a way that everything downstream of the receptacle is protected by the GFI. This would not normally be done with the interior and exterior devices, but I have seen some goofy configurations in the past. You would simply have to reset the recptacle. Other than any obvious conditions, there could be loose connections(common with older aluminum wiring) that have burnt off in a junction box somewhere. These loose connections are the common cause of electrical fires.
Whatever you do, respect the voltage
My thoughts exactly! The Bozo that wired my house put the outside outlets, the garage, and the outlet over my water heater in my utility room all on the same GFI. It justs happens that my internet feed is in the utility room too, so when something pops the garage GFI, my internet goes out. He also wired all the bathrooms on one GFI, so when the powder room pops, I have to reset it on the opposite end of the house, in the master bathroom. Idiot...
__________________
2009 KLX 250S
If it ain't broke, take it apart and find out why!
rgoers is offline   Reply With Quote
Old 05-08-2013, 02:03 PM   #13
Jayrod1318
Poster
 
Jayrod1318's Avatar
 
Joined: Jun 2011
Location: Here and there and stuff.
Oddometer: 1,522
The house must have burnt to the ground. No response from the OP.
__________________
Jayrod1318 is offline   Reply With Quote
Old 05-08-2013, 03:11 PM   #14
Heloflights OP
Gnarly Adventurer
 
Heloflights's Avatar
 
Joined: Apr 2008
Location: Vienna, VA
Oddometer: 160
Bluhduh Interesting...

Power Co was just here, both 120V phases and neutral checked out fine.

Turns out several of the affected circuits appear to be suffering from low voltage (~80-100) which explains why bulbs are not lighting up. Power co tech was of the opinion that perhaps the main panel breaker may be crapping out/acting flaky, electrician on call for tomorrow....

...never a dull minute....
__________________
Cheers,


Heloflights

2008 R1200GSA
Heloflights is offline   Reply With Quote
Old 05-08-2013, 04:13 PM   #15
River
Gee
 
Joined: Feb 2007
Oddometer: 156
Quote:
Originally Posted by Heloflights View Post
electrician on call for tomorrow....

.
__________________
Everyone has their own rhythm....so find it and lets jam
River is offline   Reply With Quote
Reply

Share

Thread Tools Search this Thread
Search this Thread:

.
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On

Forum Jump


Times are GMT -7.   It's 04:00 AM.


Powered by vBulletin® Version 3.8.5
Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.
Copyright ADVrider 2011-2014