Old 05-08-2013, 04:21 PM   #16
burnham
Oddometer: 88
Originally Posted by Heloflights View Post
Power Co was just here, both 120V phases and neutral checked out fine.
Turns out several of the affected circuits appear to be suffering from low voltage (~80-100) which explains why bulbs are not lighting up. Power co tech was of the opinion that perhaps the main panel breaker may be crapping out/acting flaky, electrician on call for tomorrow....
...never a dull minute....
Snap the main breaker on and then off a few times. Do it with a little vigor. Sometimes that will correct the problem for a short time, and let you know what the problem is. Sometimes the breaker won't stay on after, so be warned. Is it a Federal Pacific brand panel?
If you have the original 1973 electric service it's probably due to be replaced anyway.
burnham is offline   Reply With Quote
Old 05-08-2013, 04:36 PM   #17
beac83
Oddometer: 22
Did anyone do any work on the system recently?
Replace a switch, light, outlet? If so, possibly a loose connection/broken wire.
The house was built in 1973. Hopefully it doesn't have aluminum wire in the walls. (some jurisdictions still allowed Aluminum wiring back then)
beac83 is offline   Reply With Quote
Old 05-08-2013, 06:58 PM   #18
Heloflights OP
Heloflights's Avatar
Oddometer: 182
Main breaker snap results...
Tried resetting the main panel breaker several times before the power co arrived (some folks mentioned this technique can help restore a dropped phase) and behold the circuit did pop back to life for a few minutes....then keeled over.
No alum wire in the house, nor any recent electrical work performed.
I have a Cutler Hammer main panel, the main breaker is a C-H # CC2150 150A 2 pole 240VAC, looks like it has been there since Jesus was a baby. I am trying to imagine how a breaker would fail in this manner, I figured it would just die, not create weirdness like I am seeing...
Cheers,
Heloflights
2008 R1200GSA
Heloflights is offline   Reply With Quote
Old 05-08-2013, 07:08 PM   #19
Twilight Error
Going nowhere slowly
Twilight Error's Avatar
Oddometer: 22,795
A high resistance connection in the breaker would cause a voltage drop like that. The big danger is resistance = heat, enough heat can overcome the insulation and start an electrical fire in the panel.
Twilight Error is offline   Reply With Quote
Old 05-08-2013, 07:20 PM   #20
Heloflights OP
Oddometer: 182
Failing breaker - High resistance...
...wouldn't the voltage drop due to high resistance be uniform throughout all circuits in the house?
Cheers,
Heloflights
2008 R1200GSA
Old 05-08-2013, 07:38 PM   #21
troidus
Oddometer: 16,257
Not if it's just one side that's gone bad.
troidus is offline   Reply With Quote
Old 05-09-2013, 06:04 AM   #22
D.T.
Difficult but useful
D.T.'s Avatar
Oddometer: 11,893
Large voltage drop across one leg huh?
Let us know what the bill is, I'm curious.
Originally posted by burgerking So?
Holland is about the most expensive country in Europe when it comes to bikes and fuel..Stop whining and go riding It's just money and you only live once...
D.T. is online now   Reply With Quote
Old 05-09-2013, 06:07 AM   #23
rapidoxidationman
Easily trainable
rapidoxidationman's Avatar
Oddometer: 9,039
If it's just the main breaker it shouldn't be much. The cost of the breaker plus an hour of time. If the electrician spends a bit of time making sure everything else is good then bump it to two hours... couple hundred bucks max?
Patrick:
I know I'm feeling badly when I have no interest in speeding
rapidoxidationman is offline   Reply With Quote
Old 05-09-2013, 06:38 AM   #24
Al Tuna
PUI... Deal with it
Al Tuna's Avatar
Oddometer: 14,159
The 150 amp main breaker alone, will run about a hundred bucks. Let's hope the blades on the panel aren't burned, which could very well be the problem.
Al Tuna is offline   Reply With Quote
Old 05-09-2013, 07:02 AM   #25
rapidoxidationman
Easily trainable
Oddometer: 9,039
You can have only 150A service? The minimum a new house around here gets is 200...
Good point on the blades... Aren't those buss bars replaceable though?
Patrick:
Old 05-09-2013, 07:10 AM   #26
Twilight Error
Oddometer: 22,795
That might depend on the box manufacturer and parts availability. If the box is as old as the OP implies, those bits may not exist or be easy to find. Also, I've only ever seen 100A and 200A service, 150 seems a bit odd.
Old 05-09-2013, 07:15 AM   #27
trailNtent
trailNtent's Avatar
Oddometer: 218
If you have 120 to neutral or ground at the bus bar of the panel and have strange voltages on a few branch circuits, I can almost guaranty you have a neutral loose somewhere. Probably on a multi wire branch circuit. Start at the first device that's not working that's closest to your panel and look for loose neutral connections. Back stabbed receptacles are usually the cause of this.
trailNtent is offline   Reply With Quote
Old 05-09-2013, 08:12 AM   #28
Jayrod1318
Poster
Jayrod1318's Avatar
Oddometer: 1,640
I found a replacement antique one at the local recycled building material place for $1.50.
Otherwise it would have been 100+ bucks for the 100 amp breaker.
Alternatively I could have replaced the main separate breaker box for about 85$ with a new breaker and all. Although that would have required calling the power company and having my service disconnected.
Jayrod1318 is online now   Reply With Quote
Old 05-09-2013, 08:53 AM   #29
Heloflights OP
Oddometer: 182
Update....
I found a new main breaker, $170.
I have two 150A boxes, the 2nd box is dedicated to the AC and furnace.
When I reset the main yesterday and the flaky circuits returned briefly to life all voltages read nominally on the affected outlets and light fixtures.
Electrician is supposed to be here this pm....breaker is on order as well...it won't be here until tomorrow however...
Cheers,
Heloflights
2008 R1200GSA
Old 05-09-2013, 10:03 AM   #30
D.T.
D.T.'s Avatar
Oddometer: 11,893
150A for HVAC?
How many sq feet?
Hopefully the bus bars aren't burned. Then it's time for a new panel. Might be able to get just the bars. Only problem with the snap in breakers. Bolt down ones I've never seen burned.